CosbyWood wrote:
I should have taken a picture, but didn't and I just remembered that I had a question. If I don't get it out there, I'll forget and then I won't ever get to finish my project.
I have a storage area that is off of our bonus room over the garage. It was uninsulated (except for the wall adjoining the room) so I am insulating it to make it a little more bearable while at the same time laying out plywood to floor it for actual use. What I came across while doing this, which brings up my question, was the roof line that actually goes into the attic. In each little channel, there is a styrofoam type piece that goes under/through the existing insulation into the attic itself and it was somethingVENT stamped on it. I can't tell what the something says as it's completely covered under the insulation. What my question is, can I cover that? Is it venting to the attic, or from the attic? Should I extend it down to where I won't have any insulation so the venting can still take place? To many questions. If anyone needs more, I'll try to remember to take a picture tonight so I can post it. Thanks!
Yes you need to extend the little styrofoam vent channels before insulating currently exposed roof rafters. Just staple them in place to extend the ones you probably found near the floor, all the way up where you will be insulating.
You need an unobstructed air path from the soffet vents on the overhang, up along the roof rafters, and to the ridge vents at the very top of the roof. This is standard passive roof ventilation which cools the roof in summer and prevents icing in winter.